    Hey there...just wondering if anyone can give me a quick, easy, general rule of thumb for figuring out conductor and breaker sizes for roof top units. There seems to be a lot of RLA's, LRA's, FLA's, MCA's, MOCP's, Maximum Breaker, Minimum
    Fuse, etc. figures on the nameplates of these things, and I was hoping to clarify which of these are important to us, as electricians, to use. Thanks in advance [img]smile.gif[/img]

  2. #2
    Inactive Member bigrockk's Avatar
    Join Date
    September 29th, 2002
    Posts
    146
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    Check out this article, it should help you understand the nameplate data. It makes reference to the Nec and of course you will have to reference the CEC but it is a good article.

    http://www.iaei.org/magazine/99_d/simmons.htm

  3. #3
    Inactive Member CRM's Avatar
    Join Date
    February 29th, 2004
    Posts
    32
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    The label should have all the information you need, the first thing I look for is the voltage, single or three phase, minimum circuit ampacity(wire size), and maximum overcurrent protection, if possible I would go with the maximum overcurrent rather than the minimum, to prevent the breaker from tripping on startup.

  4. #4
    Inactive Member Daledo's Avatar
    Join Date
    March 5th, 2005
    Posts
    4
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    Thanks a lot guys. That's what I was trying to explain at work the other day, but the other guys were convinced that we needed to take 125% of the largest motor (the compressor) then add the other motors for the conductor size. I told them that it was already calculated in...now I have a website I can show them. Cheers [img]smile.gif[/img]